camerontech wrote:
to rephrase the question, we're using 8'x16' foot slabs to cover the hole and the actual clear span is 10' (so about 3' on each side will lay on a compacted rock floor) I just got the yield rebar strength as an estimate really, you can assume standard rebar spacing if you want, I'm not too familiar with it.
Once you have a thickness, there's too things you have to consider - bar size and spacing (obviously, larger spacing means larger bar size). Your yield strength is reasonable for structural steel, but a little low for rebar - usually it's about 60000 psi.
If your clear span is only 10', you can get away with a 7" bar spacing, assuming you use the 20M bars. You also typically want to have some bars placed in the perpendicular direction - 10M at 6" or something like that.
That being said, if there's a significant possibility that the slab will be driven on, you should ask your higher ups to call up an engineer to do up a drawing for you - the only thing worse than an open pit is a poorly design cover that will fail when a logging vehicle operator thinks he can drive over it.
The specs I gave should only be considered a general guideline - don't use it without confirming it with someone you work with professionally.